AGM Battery Resting Voltage

Last year I purchased a set of 4 Rolls S12-230AGM-RE batteries.  They've been installed since October and working great since then.  I don't have a problem but instead I'm observing something that doesn't seem normal (at least in my experience).

For the past month, the batteries have been "at rest" meaning there is no charge or discharge on them.  Also for the past month, I've noticed that their total voltage has remained at "52.0V" all that time.  I think I was expecting them to rest at about 50V, maybe a bit higher.  Converting to a per-unit measurement they average: 52/4 = 13.0V each.  Is this normal for an AGM battery?

Ruling things out:  The two different sources that could recharge these batteries (an inverter and a wind turbine) have been disconnected at the breaker and shut down, respectively.  There haven't been any unusually hot or cold temperatures here (Calgary).  The batteries power a little LCD voltage meter that's been displaying "52.0" plus or minus 0.1 all this time, but that's a phantom load, not something that would supply a charge.

I've consulted some data for these AGM's on the Rolls website's support pages.  I found a chart of open-circuit voltage versus SOC which suggests that 100% SOC has a resting voltage of 12.8 to 12.9V, which is getting close to what I see.  But that's for 25degrees C, and these batteries live at ambient temperature, which is more like 0 - 10 degrees C in the spring. I should add that I don't think these batteries really were at 100% SOC when they were disconnected. In early April, the temperature would have been about 5 degrees C, meaning the maximum SOC would have been about 90%.  If I made a prediction based on this information, I would expect 12.6V * 4 = 50.4V today.  The same charts show that self-discharge isn't a factor at these temperatures (which is great).

Does anyone see anything unusual about 52.0V?
(or 13.0V per battery, I should say?)
6.5 kW PV solar array + 12k Sol-Ark Inverter
10ft (3m) diameter custom-built wind turbine

 

Re: AGM Battery Resting Voltage

Reply #1
My smaller 100ah agms rested at 12.6 volts...

have you measured at the batteries with a calibrated voltmeter? Cheap voltmeters can drift off calibration.

Another thing to check if the wire run between batteries and voltmeter is long and/or if it passes near any transformers... I had to use shielded cable to my Tristar TS-RM-2 meter(remote meter for the MPPT45/60 charge controllers) because it would pick up voltage when I transmitted on my ham radio and then stay reading high until I unplugged it for awhile.

Re: AGM Battery Resting Voltage

Reply #2
I can't claim any of my VMs are calibrated.  But I have 4 of them.
6.5 kW PV solar array + 12k Sol-Ark Inverter
10ft (3m) diameter custom-built wind turbine

Re: AGM Battery Resting Voltage

Reply #3
On the most trustworthy true RMS meters:
Meterman 37x: 12.94+12.96+12.95+12.97 = 51.82V
Fluke 374 clamp with leads: 12.9+12.9+12.9+13.0 = 51.7V

Earlier today I did some troubleshooting on the Tristar charge controller.  It was pulling 25Amps out of the batteries for a while in "Load control" mode during my tests, which has cut down the voltage from 52.0 a little.
6.5 kW PV solar array + 12k Sol-Ark Inverter
10ft (3m) diameter custom-built wind turbine

Re: AGM Battery Resting Voltage

Reply #4
On the most trustworthy true RMS meters:
Meterman 37x: 12.94+12.96+12.95+12.97 = 51.82V
Fluke 374 clamp with leads: 12.9+12.9+12.9+13.0 = 51.7V

Earlier today I did some troubleshooting on the Tristar charge controller.  It was pulling 25Amps out of the batteries for a while in "Load control" mode during my tests, which has cut down the voltage from 52.0 a little.

So close to where mine rested... I would say nothing wrong...

Re: AGM Battery Resting Voltage

Reply #5
Thank you
6.5 kW PV solar array + 12k Sol-Ark Inverter